Have a Trane central system installed in 88. Model T V030 A140A0
When I last ran the A/C a few months ago it seemed to be working fine. Usually when it fires up, you can hear a shursssshhhhh-shurrssssh which I gather is freon starting to move within the system and you can feel the bubbles in a tube at the front of the air handler housing.
Now when I fire it up I get no freon sound and no cool air. The air handler is funning and the fan on the compressor unit outside is running. I depressed the Hi Press fitting a really quick hit just to verify there's pressure and there is.
It actually exhibited this behavior years ago when it was newer - a few restarts seemed to get it kicked into gear, but so far no luck.
I'm not versed in A/C but am otherwise mechanically inclined, no problem whatsoever digging into things with proper direction. Any primary suspects I should look at before calling someone in?
Thanks for all input.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

If there is any Freon (refregerant gas) in the system, it will have pressure. YOu need to verify the compressor in outside unit is running. There is probably a relay that will pull in to power the motor when it starts up. A clamp on amp meter would tell if the compressor motor is drawing current.
In simple terms the compressor is going to compress the gas, it goes to the outside coils and is condensed into a liquid as it gives up the heat to the outside air. It then goes inside and absorbs heat from the inside coils, boils in doing so and back to the compressor.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Its 22 years old... they don't last forever....especially when they are not serviced regularly.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

It's not clear what "servicing" it needed. Turned it on, it worked.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Your local HVAC people can tell you.
--
Christopher A. Young
Learn more about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

It's not clear what "servicing" it needed. Turned it on, it worked.
You turn on your car and it works... do you ever have it serviced?? after all your probably not driving it but maybe an hour a day, and you buy a new one avery couple of years..... Your heating and cooling system is the single most expensive appliance in your home, and it runs 24/7....and you never have it serviced??
Here's a BOHICA moment for you.... the cost of the typical system replacement these days (not including any ductwork) is going to cost anywhere from $5,000 - $15,000. I hope you got some money put back....your gonna need it.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I do all my own auto servicing. There are specific pieces that are subject to wear, corrosion, sacrificial fluids that need replacing.
It's my understanding that the "lubrication" in an A/C compressor is contained within the freon, that if it has freon it's got lubrication. Does one "change the oil" in an A/C system?

Actually, mine only gets run sporadically. I don't run it day in, day out. Only when it get hot or cold enough and only when I'm actually home. There are probably people who run theirs more in a year than I do in 5.

Can you specify what servicing could be done to it to make it last longer? Not being facetious, just seems that an auto and an A/C system are different animals. I don't do "maintenance" on my computer hard drives either, other than occasional defragging and antivirus scan. But there's no actual mechanical "maintenance" to be done.
The word I keep hearing about many A/C companies who solicit for "maintenance" is that many are shady, similar to companies who tell you you need to put "treatment" in your septic tank, etc.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

I do all my own auto servicing. There are specific pieces that are subject to wear, corrosion, sacrificial fluids that need replacing.
It's my understanding that the "lubrication" in an A/C compressor is contained within the freon, that if it has freon it's got lubrication. Does one "change the oil" in an A/C system?

Actually, mine only gets run sporadically. I don't run it day in, day out. Only when it get hot or cold enough and only when I'm actually home. There are probably people who run theirs more in a year than I do in 5.

Can you specify what servicing could be done to it to make it last longer? Not being facetious, just seems that an auto and an A/C system are different animals. I don't do "maintenance" on my computer hard drives either, other than occasional defragging and antivirus scan. But there's no actual mechanical "maintenance" to be done.
The word I keep hearing about many A/C companies who solicit for "maintenance" is that many are shady, similar to companies who tell you you need to put "treatment" in your septic tank, etc.
Your car and you A/C both have moving parts, they both have filters, they both have electrical systems, they both have blowers and fans. Your A/C also has to have the refrigerant charge balance checked once everything is clean and verified to operate properly so that it is operating as it was designed to, as well as making sure that it has no refrigerant leaks.
BTW.. the refrigerant in your system is being "phased out". In the next year, the price of that refrigerant is going to be 8 - 10 times higher because of the most recent 75% reduction in production and importing of R22
As far as "shady" companies, do a little homework.... talk to friends, family, inlaws, outlaws, folks you go to church with, etc..... ask them who they use or don't use, and why.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

The outside unit could have just the "fan" running, but do you hear the compressor? The contactor might be corroded/intermittent. Give it a whack and see if the compressor kicks on. Could also be a bad capacitor.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 5 Apr 2010 17:43:25 -0700 (PDT), brassplyer

The only servicing a residential a/c ever needs is a clean filter a few times a year and hose out the condenser after the cotton woods quit making cotton. That's been my sure fire winner for over 20yrs with mine. Or you can pay some Stormy Mormmy type simpleton to come out and hook up their nasty gauge set every year, contaminate the system and let a little gas out when they disconnect and charge you out the ass for "the service".
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Right, exactly what I've been doing. And a couple of times I've had to blow out the drainage line when it got clogged with gunk.

Which is exactly what I've heard and why I've avoided having anyone "service" it. I've gone under the assumption that since once fired up it cooled the house off quickly and could easily get it colder than I needed, things were working as they should.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Right, except if someone stole the refrigerant out of your outside heat pump unit... Or something finally corroded through after 22 years of being outside in the elements... Or maybe you don't cover your outside heat pump unit during the winter and ice built up inside of it and snapped something letting the refrigerant gas escape...
In every trade there are good companies and bad... Don't lump them all in with the bad... It is obvious that you don't have a clue what to look for when you "hose down your condenser" and wouldn't know how to find a refrigerant leak if that is what your problem is...
Stop being cheap and hire someone to come out and give your AC unit an look to see what is wrong with it...
~ Evan
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

In which case it would be "BROKEN" and need fixing. I agree with the other posters, servicing is just a money making operation.
The OP probably needs someone to take a look at but not because it needs servicing, because it's broken.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

And if AC units need professional servicing, including checking the refrigerant level, why is it that refrigerators, which are very similar refrigerant systems, don't? All you need to do is change the filters and clean out any leaves from the compressor unit. And if servicing is so critical, how is it that the OPs lasted 22 years, which is the full life, without it? You can't compare this to car maintenance. If you didn't change or check the oil in your car, it surely wouldn't last 22 years.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Apr 6, 8:36am, snipped-for-privacy@optonline.net wrote:

Why ??
Because a refrigerator only keeps a small very well insulated space cold... Your home AC unit (which is only about 3x the size if you look at the internal components compared to a refrigerator) is working MUCH harder to cool off an exponentially larger volume of space in comparison to the interior volume of your refrigerator...
As to your other ponderings about why his AC unit lasted so long without requiring repair, who knows, could be he hardly ever uses it like the OP claimed in previous posts, could have been luck... A car could conceivably go 22 years without an oil change if you drove it less than 4,000 total miles during that time... I don't know of anyone who owns a car that they "hardly ever drive" over more than 20 years of owning it, do you ???
And no, you don't know enough about AC units if all you think you need to do is change the filter in the duct work and clear out the leaves from the outside heat pump... You really should be inspecting the coils inside your duct work and CLEANING those of dust and debris annually so that the air passing through the coil in the duct can be more efficiently cooled... You should also clean the coils inside the heat pump annually as well as dirt, bugs and any number of things can get inside the fins and restrict airflow... When you shut off your AC system each year you should be covering the heat pump unit outside to PREVENT debris like leaves from entering it and to protect it from ice getting inside the unit during the winter...
~ Evan
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Covre the heat pump outside during the winter? Doesn't really heat very well when you do that does it?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
The OP stated that he was using it for cooling only.
--
Christopher A. Young
Learn more about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

My method - disconnect power from unit at the outside breaker and main breaker. Take top grill/fan piece of condenser housing. Pull plant crap out by hand and/or with a shop vac, hose down the coils to remove other crap. Anything wrong with this?
Unit was working like a champ the last time I fired it up a few months ago. Cooled off the house quickly. Sound like maintenance was obviously called for (as of that time) to you?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

My method - disconnect power from unit at the outside breaker and main breaker. Take top grill/fan piece of condenser housing. Pull plant crap out by hand and/or with a shop vac, hose down the coils to remove other crap. Anything wrong with this?
Unit was working like a champ the last time I fired it up a few months ago. Cooled off the house quickly. Sound like maintenance was obviously called for (as of that time) to you?
-------------------------------------------------------
Naw..... just run it till it quits, then get ready to shell out the big buck$$$$
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Yup... BEFORE you start it up for the new season you should do maintenance on the entire system...
Just because something was "working like a champ" the previous time you operated it has no bearing on any number of things that have happened to it since your "well it worked the last time I used it" situation...
Has it rained since the last time you used your AC unit ??? Could have had a lightning strike nearby that fried an electrical component inside the heat pump...
If your idea of "maintenance" is just cleaning it out periodically then you have no clue... Preventive maintenance is the cumulative effect of doing small things much more often to allow the equipment function normally without having to struggle to keep up with demand because of dirty and clogged coils... It also requires more care than turning off a switch in the fall and a few minutes under your wet/dry vac in the spring...
Count yourself as lucky that it lasted 22 years...