My old home (50's) has, for the main part, no ground wires running to the outlets. The wiring is romex, but, only a hot and a neutral except where I have added additional outlets. The previous owner has placed three hole (grounded) outlets on many of the two wire circuits. I know that is not to code and should be converted back to groundless plugs.

Question: Can I simply run separate ground wires to these outlets. Almost all of the wiring reaches these outlets via the attic crawl space. Do I need to make 'home runs' to each outlet or can I install splice boxes in the attic and do radial runs from therein?

All advice or criticisms appreciated.

Thanks, Ivan Vegvary

Reply to
Ivan Vegvary
Loading thread data ...

Yes, as per NEC 250.134(B) exception #1. You can access the 2005 NEC online through a java applet via:

Home runs are not required. For a retrofit application like this, you could daisy chain all the equipment grounding conductors (EGC) in a single run.

Cheers, Wayne

Reply to
Wayne Whitney

id do only the ones needed, most things dont have a ground prong anyways, computer, fridge strove, washer thats probably about it. most of those have a metal shell is why they are grounded.

Reply to
sym

See NEC 2005 250.130C & 250.130C

formatting link

Reply to
SRN
250.130C

OOPS, should have said see NEC 2005 250.130C and 406.3D(3)

Reply to
SRN

I have the same problems with a 50's house. Can you give more detail how to retrofit daisy chain and especially where to buy the grounding conductors (ESG).

Thanks

Reply to
John JJ