Kathy wrote:

requirements apply to New constructions and new installations on existing buildings:
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel. FPN: See 215.9 for ground-fault circuit-interrupter protection for personnel on feeders. (A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel. (1) Bathrooms (2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use Exception No. 1: Receptacles that are not readily accessible. Exception No. 2: A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8). Receptacles installed under the exceptions to 210.8(A)(5) shall not be considered as meeting the requirements of 210.52(G). (3) Outdoors Exception: Receptacles that are not readily accessible and are supplied by a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed in accordance with the applicable provisions of Article 426. (4) Crawl spaces at or below grade level (5) Unfinished basements for purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like Exception No. 1: Receptacles that are not readily accessible. Exception No. 2: A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8). Exception No. 3: A receptacle supplying only a permanently installed fire alarm or burglar alarm system shall not be required to have ground-fault circuit-interrupter protection. Receptacles installed under the exceptions to 210.8(A)(5) shall not be considered as meeting the requirements of 210.52(G). (6) Kitchens where the receptacles are installed to serve the countertop surfaces (7) Wet bar sinks where the receptacles are installed to serve the countertop surfaces and are located within 1.8 m (6 ft) of the outside edge of the wet bar sink. (8) Boathouses
Item 3 is pretty clear, if it is outdoors, it MUST be GFCI Protected.
Hope this helps.
Don
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

You're right Don. Being a biased customer of a home builder(I live in one), I have a really hard time believing that a regular receptacle outlet outside was missed, even two. Makes really concerned about what else they missed, if the obvious stuff was overlooked.
:(
later,
tom @ www.Love-Calculators.com
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Related Threads

HomeOwnersHub.com is a website for homeowners and building and maintenance pros. It is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.