I had a garage built and am wiring the building with 200A service myself. At Lowe's, they have a sign that says the lead-in cabling for

200A service needs to be 4/0 - 4/0 - 4/0 - 2/0 aluminum cable. But, one of their workers says that is wrong that the service cable must be that size, but in copper. Anyone know for sure?
Reply to
Rick
Loading thread data ...

Dont do the work yourself, and don't hire that HD worker to do the work.

Get a qualifed electrician, since from your post I'm not sure if you want a new service, or a subpanel.

later,

tom @

formatting link

Reply to
Tom The Great

You don't provide enough information to answer the question. Is this cable to be used before or after the first disconnecting means? Is the service to your home to be single phase or three phase? Is the service supplied via overhead or underground conductors?

Reply to
Tom Horne, Electrician

OK Fer Sure, you need 3/0 copper or 250 Kcmil aluminum for the feeder to a 200a sub-panel unless it is the main feeder for a "dwelling". A garage is not a dwelling so 310.16 applies.

Reply to
gfretwell

Reply to
Rick

The cable will be before the first disconnect. It will lead from the connection point where the electric company will provide service up to the meter base and then from there into the main breaker panel. The main service disconnect is on the main breaker panel. The service is three-phase and underground.

Thanks

Tom Horne, Electrician wrote:

Reply to
Rick

Rick wrote: > The cable will be before the first disconnect. It will lead from the > connection point where the electric company will provide service up to > the meter base and then from there into the main breaker panel. The > main service disconnect is on the main breaker panel. The service is > three-phase and underground. >

gfretwell has answered the question. The cable you described in your original post is suitable for the single phase feeder between the main disconnecting means and the lighting and appliance panel board/s in a residence but it is not allowed for the service entry conductors of a three phase two hundred ampere dwelling service.

Reply to
Tom Horne, Electrician
2/0 is sufficient for 200A in copper.