Electrical ground fault

I have a circuit which has no power even though the breaker is on. The power stays off for several months, then suddenly goes back on. Several months later, it suddenly goes off. I haven't noticed any triggering events.

The electrician I've been using tells me its a ground fault and can only be checked when the power is on. He goes from outlet to outlet, fixture to fixture, testing but never seems to find anything. I'm not even sure what he's testing! I've forked over a ton of money to this guy and still have a problem.

Does this sound reasonable, or should I be looking for another electrician? I wish I could re-wire, but it just isn't in the budget right now!

Reply to
nj_dilettante
Loading thread data ...

I would try a different electrician. The cable going to this dead outlet has to come from somewhere, and depending upon the location of the dead outlet, such as outside or in a bathroom, it should give a clue to where to look for the problem. It sounds like a loose connection, but the devil is finding where

Reply to
RBM

Has your electrician pointed out to you where there are GFCI devices "protecting" that circuit, such as a GFCI breaker in your home's breaker panel or a GFCI receptical fed by that circuit, which in turn feeds other devices "downstream" of it?

If he says it is a "ground fault", then he ought to show you how to try and reset the breaker or receptical when the power "dissappears".

HTH,

Jeff

Reply to
Jeff Wisnia

It's not one outlet, it's an entire circuit which (unfortunately) services PARTS of 3 bedrooms, 3 bathrooms, the den, the upstairs hall, a couple of basement lights and all of the finished attic. No GFCI on the circuit. My house is a 200-year old monster which was re-wired - not by us - in the

1970's. I have 28 circuit breakers in the box, but almost half the house is on this one damn line!

I really would like to know if "ground fault" is a reasonable diagnosis, and if so, how one would go about finding the problem. I've found it difficult to get an electrician in for this - all of them here in central NJ are too busy with new construction to want to be bothered with a nasty problem in a old house.

Reply to
nj_dilettante

Reminds me of that TV commercial where the guy is flipping this switch in his garage and hollering to his wife "is it that one honey" while two doors away a garage door slams up and down on some old lady's car (presumably controlled by his switch).

Ground fault means current is traveling from the hot into the ground conductor, while this may trip a regular breaker and will trip a GFCI breaker or receptacle, it generally does not cause intermittant operation with random occurance and long MTBF. A ground fault could be found with the power off and an ohmmeter between hot and ground. He is limiting his test method to the one tester he understands (the plug in tester I would guess)

Now if he were looking for an open neutral or hot in a wire nut that occasionally makes contact when enough vibration gets in the wall, that would be more reasonable.

Is the whole branch circuit blacked out at once or just a portion of it? It could take a little time to map out the cables in the walls without seeing them so one could predict the location of an open. Has he tried the simple, lets replace the $20 breaker and see if that helps approach.

Seriously, you should only pay his on site estimate fee (usually the first hour labor or so). If he cannot find and fix a problem, he has not rendered a service that is billable. If he ultimately fixes it, he is justified to bill for time spent but if he gives up, the additional time wasted should be his. Don't pay as you go, he could give up at any time and you will be at square 1 without a head start.

Find another electrician, not one who works alone or with just 1 or two partners. Get one of those 1-800-plumber/electrician outfits from the yellow pages. The pricing is less flexible but in this case that is to your advantage. Most times they will give you a fixed price quite and there are several levels of managers to climb if there is a problem, If the "technician" or Journeyman electrician can't find it Demand they send the Master out.

If it is working now and you are looking back in time trying to find the fault, that could be very difficult. Might wait until it blacks out again to start troubleshooting.

Reply to
PipeDown

Since you have no ground fault circuit interrupters, a ground fault isn't your problem. If the circuit breaker is tripped and won't reset, it's a short circuit. If the circuit breaker is on and current is going through it, you have an open circuit. This problem makes sense in an old house. When this house was first electrified, they probably had one circuit that went to a few locations all over the house. Over time people kept tapping that circuit whenever they wanted to add new outlets and lights, so now you find

90% of the house is on that one circuit. What you really need to have done is an additional line brought from your panel and feed that part of the circuit.

Reply to
RBM

The circuit breaker is on, but there is no current anywhere on the line. One wing of the house was made into an apartment in the '40's, and this was also on the bad line. We had that rewired to a separate panel about 10 years ago - this on/off problem only happened about 2 years ago. So load shouldn't be a problem since we have considerably LESS drain on the circuit now than in the past.

Reply to
nj_dilettante

Then measure the voltage at the breaker itself (output screw to neutral bus). if the breaker is on and there is no voltage, the breaker is bad if there is voltage, you have an open in the first J box it goes to (unless someone put a splice in a concieled location, now we would know why not to do that).

Check that the wire nuts in the first J box on that branch are all in good tight condition. May need to open them (splice at a nut) to inspect wires for damage or corrosion. If there is no voltage from hot to neutral or ground at the first J box then you have the unlikely failure of a wire along its length (possible Nail intrusion)

If you cannot deduce the location of the cable or first J box on the branch, you will need to use a signal tracer to follow it inside the wall from the source at the breaker panel.

Here is one reasonably priced tracer that can be used for LAN, phone and AC (with hot disconnected at the panel). Others are available optimized for AC if you look around

formatting link

Reply to
PipeDown

THANK YOU! This is just the advice I was looking for! Which means, basically, that you've justified my doubts about my electrician, and you've given me some vocabulary to use with the next one.

My BS radar has been beeping loudly and I've been longing to ask this guy if my problem will be fixed before his youngest kid is out of college! I'm a woman who knows enough (after 15 years of renovating a very old house) to hold my own with most trades, but I have not been able to get a handle on this problem.

Reply to
nj_dilettante

Try Opal Electric (908-245-3577) in Hillsborough. Never had them do any work but the guy came out the day after I called them to give me an estimate.

formatting link

Reply to
RayV

Oh, s**t. Please tell us they did *not* use aluminum wire. Please.

Not evidence of a good job, I'm afraid.

Not in my opinion. I think it's much more likely that there's an intermittent connection somewhere. And if you have aluminum wiring, that is _very_ dangerous.

Got any friends who know their way around residential wiring? The solution to the problem may be nothing more than opening up every junction, switch, and receptacle box on the circuit, one at a time -- with the circuit OFF -- and checking manually for loose connections.

Reply to
Doug Miller

I agree completely.

formatting link
informative site.

Reply to
RayV

easiest fix is to first split the circuit add a breaker. then find if the old part or new part fails again.

in any case the time to troubleshoot it is when its failed.

for such a $^%$ makre a drawing of what feeds what starting with the breaker finding the first outlet in the string. use ohm meter with power OFF

once you have a complete map, the next time it fails you check each outlet looking for where its first out

you electrician may believe its a neutral failure, but taking apart each box is probably the first step