electric dryer question

Page 2 of 2  
wrote:

If you actrually read the old 250.50 it says you are using the neutral conductor for grounding. Some (most?) inspectors said this had to be a white insulated wire unless you used the exception that allowed SE cable. It was never legal to use 10/2 wg Romex for a dryer. It was also never legal to feed a 3 wire dryer or range plug from a sub panel. It had to come from the main panel where the ground electrode connected.
You should really look at the wire. You may find that it was actually wired with 10/3 romex and the ground wire is connected to the box (a common method) or cut off at the jacket. In either case you can probably get enough slack to connect the 4 pin receptacle. If it is SE cable (or 10/2 RX) you are stuck with the 3 pin.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

My mistake It was 250.60
Here is the text from the 96 code
250-60. Frames of Ranges and Clothes Dryers.
    
     (b) The grounded conductor is not smaller than No. 10 copper or No. 8 aluminum.
     (c) The grounded conductor is insulated; or the grounded conductor is uninsulated and part of a Type SE service-entrance cable and the branch circuit originates at the service equipment.
    
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload