I'm not an electrician or anything But I did stay at a Holiday Inn Express double taps on a circuit breaker NOT allowed (two hot wires under one screw) And i'm sure pigtail in breaker box is not allowed

Reply to
Spud
Loading thread data ...

This really falls back to the manufacturer's instructions. Some 15, 20 and 30a breakers are marked to accept 2 conductors. (NEC article 110.3(B))

You can splice 2 wires to one, even in the breaker enclosure, if there is enough space. (NEC article 312.8)

Reply to
gfretwell

To make a long story short ... About 10 years ago had an electrician add a subpanel in my then new workshop (state of Virginia). He placed a 30 amp breaker in my main box and used that breaker to feed the subpanel in the shop. Wiring was run in such a way that if 220v was ever needed it would be a simple matter to get it to the work area. Now I am attempting to sell my house and the inspector says "double taps on a circuit breaker are not allowed." I think the electrician just placed the "extra" wire there to keep it from floating around in the panel but leave it available if 220 was ever desired. I guess I have 3 questions.

Are double taps on a circuit breaker against the NEC?

If double taps are permissible under the NEC, does anyone happen to have the reference handy?

If it is against the NEC, can a pigtail be used to join the 2 wires and then connect the pigtail to the circuit breaker?

Would appreciate any other thoughts. Thanks a bunch.

Reply to
Roger Morton

A pigtail is equivelent to coming out of the box on one wire and then branching to more than one fixture which is premitted so long as there are not too many loads which would require another circuit anyway. Connect pigtail outside the breaker box and inside a seperate J-box and it should be good. Not sure, but it may be just a matter of putting two wires in a connector made for one.

If you have a wire leading somewhere that may be used in the future than it should be taped off and labeled "future" inside the box but not connected to a breaker just to keep it captive. What about the other end of the wire, is there a receptacle? Shouldn't be live if not. If he really wanted to restrain a loose wire, it should be connected to ground or neutral. I must be misunderstanding the reason for the double tap in the first place cause that don't make too much sense.

Reply to
PipeDown

Yes unless the breaker is listed for 2 wires.

As far as I know only Square D breakers 12-20-30 are UL listed for 2 conductors per breaker screw.

Agree. This is a realy simple solution. It is unlikely the side gutters are too crowded already.