If I remove panel cover to check circuit breaker and using a screwdriver type of tester see if light goes on when the breaker switch is on and it goes off when the switch is off...Does that mean the breaker is working or is there more involved? Thanks.

Reply to
harry manka
Loading thread data ...

Yes. There is more. You are only testing that the breaker can be turned on and off. You did not test to assure that it will turn itself off when it gets and overload, nor did you test to see if it might turn off at the proper overload. Old breakers often start triggering early so they shut down the circuit under normal load.

BTW a breaker that fails to shout down the circuit with an overload is very rare.

Reply to
Joseph Meehan

There are circuit breaker testers made for every manufacture that I am aware. Problem is that they start out at about $5k and go up from there. When I was a field service engineer the company owned about everything that was available. The smaller test sets for plug-in breakers, residential types, were the least accurate. Check out NEMA for specs on testing breakers. That is the most stringent spec that I know.

Buying a new breaker will be easier and cheaper than testing molded case breakers below 100 amps.

Reply to
SQLit

Assuming this is a 15 or 20 amp breaker, you could cause a deliberate short, and see if it trips.

I wouldn't do this on a bigger breaker, too much current there.

Shut off the breaker, connect a short piece of wire to it, turn back on, touch wire to ground (metal box), breaker should blow.

Cost $0.20 (2 ft of wire at 10/c a foot). Watch out for flying sparks.

Reply to
John Hines

If the withstand rating of the breaker is inadequate for the fault current that the fault you are creating then the breaker may fail explosively. If you look at the breaker you will find the withstand rating expressed as X AIC were X is the number of amperes of fault current that the breaker has been tested to interrupt without failure. If the transformer that supplies your home has been replaced with a larger unit to keep pace with neighborhood demand the available fault current may exceed the rating of your panel or the breakers that are installed in it. My last service upgrade was from a relatively small transformer only one span away from the drop and the available fault current was 8800 amperes. If the transformer had been on the same pole as the drop the withstand would have needed to be upgraded above the

10,000 ampere value of the stock breakers.

In other words if you don't know what the available fault current is then dead faulting a breaker is a DAMMED STUPID THING TO DO!

-- Tom H

Reply to
Takoma Park Volunteer Fire Dep

If a normal household breaker can't withstand a short circuit, it is bad. Create it any way you like, but that is it's job, to trip and not explode, in that situation, a short circuit.

Reply to
John Hines

John, I have to agree with Tom it "is a DAMMED STUPID THING TO DO!"

Reply to
Joseph Meehan

A normal breaker has a maximum amount of fault current it can interrupt without damage. This is called it's withstand rating. The current it is capable of withstanding without damage is labeled right on the breaker. If there is more fault current available then the breaker is built to withstand then the breaker will fail. If the fault current is high enough it will fail explosively and bury parts of itself inside the eyes of the idiot who dead faulted it. You are welcome to continue to test your own breakers in the way you have recommended but to advise others to do so is negligent. Many breakers in homes have had there withstand ratings surpassed by the increase in available fault current caused by changes in the supply network brought on by increased demand. Faulting a breaker without knowing the available fault current is like pulling the pin on a grenade without having anywhere to throw it. You want to do that then fine but kindly stop being so reckless with the safety of others by offering such dangerous advice to people who have not the training to evaluate your competence.

-- Tom H

Reply to
HorneTD

Just plug in TWO 1500watt electric space heaters, turned on HIGH. A

15A breaker should trip in a few seconds. A 20A one should trip shortly, but it may take several seconds, up to one minute. That is the easiest way to test breakers without sparks. This method is ONLY for 15A and 20A 120V breakers. Dont mess with any larger ones, or 220V types.
Reply to
jamie

I'm not advocating shorting out the breaker, but how would one determine the available fault current at a service.

Also, if the available fault current exceeds the rated maximum fault current of the existing breakers, how important is it to upgrade them?

Mr. Fixit eh

Reply to
Steve Nekias

To test a fifteen or twenty ampere breaker you detach the house wiring, attach a multi outlet assembly temporarily, plug in two 1800 watt hair dryers, turn the first one on all the way, turn the second one on to succesively higher settings until the breaker trips. The breaker should trip in less than a minute at 3600 watts or 30 amperes of current flow.

If the withstand of the breakers is exceeded by say ten percent I wouldn't be in a rush to change them. If the available fault current is more than twenty percent over the breakers withstand rating I would have them changed fairly soon. If the available fault current exceeded say

150% of the withstand rating I would change them as soon as the replacements could be obtained. If breakers with a high enough withstand are not available for your equipment then a fused disconnect with appropriate fuses for the fault current could be installed ahead of it but the calculation of the series rating of such equipment combinations is beyond the skill of most electricians. In one case I asked the power company to run a new service drop from a pole on the other side of the house. The addition of over one hundred wire feet into the supply wiring from the transformer reduced the available fault current to below the rating of the equipment.

-- Tom H

Reply to
HorneTD

I used a heat gun, toaster oven, vacuum cleaner, and a lamp. I know the lamp doesn't use much electricity, but I wanted one just so I'd have something to see. And all my old Federal Pacific breakers worked just fine.

Load testing the breakers makes much more sense then the person who said to short them out with a screwdriver. Safer too.

Reply to
Childfree Scott

This hairdryer setup would be a safe way to test the withstand rating of the circuit breaker. How would you go about determining what the available fault current would be at a service location?

Mr Fixit eh

Reply to
Steve Nekias

Yes, it's rare. I had one that shouted down so loud that I could hear it at every outlet box in the house.

(I know; typo; you meant "shut down". But it was cute.)

Reply to
Stormin Mormon

Plug in and turn on two hair driers at the same socket? Overload that breaker?

Reply to
Stormin Mormon

Deliberate overload is safer. Two hair dryers, or two plug in space heaters on same socket.

Reply to
Stormin Mormon

Successful test! Roger that, mate.

Reply to
Stormin Mormon

The failure mode of FPE breakers is unique enough that tripping them out on overload will not assure that they will trip under fault conditions. If you do a search of the Consumer Product Safety commission's site you can find more information.

-- Tom H

Reply to
HorneTD

According to John Hines :

Of course, but...

If you blind yourself or burn your house down and kill your whole family to test the thing, at least you'll know what the cause was.

Finding out that it _can't_ safely trip a short circuit by deliberately short-circuiting it is very very dumb.

Reply to
Chris Lewis

According to Takoma Park Volunteer Fire Department Postmaster :

I'll say.

I've seen a high fault like this trip fuses. Okay, the fuses were good.

Sorta.

The fuses "tripped" by exploding and the panel bus bars arced over thru the resulting plasma cloud.

Which melted a whole floor-to-ceiling panel section, started a fire in the power distribution vault and another fire in the distribution transformer outside the building.

Deliberate short circuiting is always a bad idea.