Bryant Plus 90 furnace Inducer Motor Noise

Hello all

Our Byrant Plus 90 furnace, installed in 1992, has developed an intermittent noise in the inducer motor that interferes with normal furnace operation. The symptom is loud "vibrating" type noise when the furnace is attempting to fire up to heat the house.

When I hear it the sound, I can open the furnace door and lightly tap on the inducer motor, the sound goes away and the furnace then proceeds to work normally. Then, anywhere from 1 to 10 days later, the same thing happens again..

My questions are: What do you think is going on? What would be the appropriate repair? What would the repair typically cost? Repair to be done by a professional, not by me.

Thanks in advance for any ideas on this.

Reply to
KC
Loading thread data ...

intermittent

Reply to
Anthony Diodati

intermittent

Motors shot...sheesh...it had a 10 year life expectancy, and look at it.

Replace it...

About $200, or less, or more, depending on the model of the unit needed.

Reply to
CBhvac

Anthony and CBhvac

Thanks for the info. Since '96 it has averaged a $200+ repair every couple of years. Spent about that much last, year, looks like it's breaking the pattern and going for two years in a row with this new problem. So much for the energy savings. The number of repairs since '96 seems excessive to me, but maybe because of the computer and all complexity of the system, that's a typical amount of repairs for a furnace this old..

professional,

Reply to
KC

Wow, that is allot of repairs! I have a York 90+ that was installed in '92 that has cost me $6 in parts total! Greg

Reply to
Greg O

Greg

Either you are incredibly fortunate, or we just happened to get a lemon.

It's not like the furnace is being abused. It's got an electronic filter which we clean every month. Beyond that, there's not much owner maintenance we can do (according to the owner's manual). Not sure what the pre-season tune-ups involve, but we had that done a couple of times, too. I do live in the Midwest, so it is in use for 6 - 7 months a year.

KC

Reply to
KC

Reply to
Tony Hwang

| Either you are incredibly fortunate, or we just happened to get a lemon.

I had one installed in 94. The first failure was the tuning valve (seal leaked). I noticed the water dripping onto the floor of the burner compartment and dribbling down onto the blower. At that time the unit was covered by a maintenance plan with a spinoff of the gas supplier. They had been quite helpful with the previous furnace, but they didn't seem to want to deal with this one. The tech first tried to claim that dripping water is normal for high-efficiency furnaces. Then he said he would replace that part. A few days later he called me to ask if I knew a contact number for Bryant(!). I gave him the 800 number, but I never heard from him again. Needless to say we didn't renew the maintenance plan. Fortunately I was able to order a new tuning valve (it's really just an adjustable cap) online. I still have the old one and I may try to rebuild the seal at some point.

The next failure was the internal drain tubes. They rotted out and started leaking more water onto the floor of the burner compartment. I couldn't find any specific replacement part for them so I used some transparent high-temp tubing similar to what I've seen in other brands of condensing furnaces. The original tubes were a black plastic/rubber that was more flexible but seemed to be attacked by the condensate and reduced to goo.

The next problem was a failed hot-surface ignition module. This was replaced by a service technician; however, I was a little curious about why it had failed so I watched the furnace carefully for a few days. This brings me to:

The next problem was in the control module. I observed that the furnace was cycling constantly when the thermostat called for heat. The burner would fire ok, but it would shut off even before the fan-on delay time. Then the fan would come on and run until the fan-off delay. Then (if the thermostat was still calling for heat) the burner would fire again and the sequence would repeat. Obviously this put a lot of stress on the hot surface module. The control module was not indicating any error codes and I eliminated the obvious causes (pressure switch, high-limit, flame sensor). To make a long story short, the problem was some failed solder joints on the control module's PC board. The load resistors for the thermostat loop are mounted a little off the board and soldered to grommets, but apparently not isolated well enough. The constant temperature cycling had broken the bond and allowed the connection to open when the resistors became warm during a call for heat. I soldered the joints a bit more completely and they have been ok for a few years. Note that Bryant eventually admitted to this problem and supposedly had some sort of free exchange program, but it was unclear to me (and to my service technician) how one might take advantage of the program.

The next problem was the blower motor. It started making horrible noises and caused the whole furnace to vibrate. The technician had a lot of trouble replacing the motor because the shaft had corroded to the fan cage assembly. (He used up all of my Dremel cutoff disks removing enough of the shaft to accommodate his clamp-on pulling tool. :) I suspect that the difficulty and the failure itself were caused at least in part by the previous leaks.

Lately the inducer motor has been making a terrible noise and vibration on startup. Once (if) it gets going it seems to be ok for a while. I suspect it will have to be replaced soon, though...

Dan Lanciani ddl@danlan*com

Reply to
Dan Lanciani

Dan

I've had similar problems, and the inducer motor on our Bryant 90 Plus furnace is doing the exact same thing as yours.

Last year when I had the HVAC company out here, they first thought the inducer motor was bad, but later changed the diagnosis to a plugged secondary heat exchanger. Replacing that came to $300 for parts and labor..

When it works I have no complaints, but that lack of reliability is a killer.

KC

Reply to
KC

maintenance

Nah..its why I like York, and when installed correctly, most units will give little to no problems. Some brands are simply more prone to failures than others

Reply to
CBhvac

Wow..aint that funny....replace one Carrier with another..LOL....

Bryant, Payne, Tempstar...= Carrier.

Reply to
CBhvac

My Bryant 90+, that was installed in '87 started squeaking. I just took the Inducer motor apart, oiled the sleeve bearings with Mobil 1 and it's quite now (That was 6 years ago). That was only repair that was done to it in 17 years.

Reply to
Keith S.

Reply to
Larry Kraus

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.