Tony Hwang wrote: ...

Quite a number--anywhere a branch circuit caused a fire and that wiring was Al would be, fundamentally, a case.

The problem isn't with the sizing of the conductor or the ampacity of the wiring; it's owing to the tendency of Al to oxidize which leads to higher resistance which causes resistance heating and the mechanical properties in which it creeps leading to reduction in fitting tightness which also raises resistance.

After about '72 when Al wiring w/ differing alloy properties started becoming available as well as an awareness of the problems and improved connectors and procedures, the risk began to go down somewhat, but it's still statistically much higher than Cu -- I believe I've seen CPSC numbers of roughly 40:50X higher risk.

--

Reply to
dpb
Loading thread data ...

No, you are US centric. Much of the rest of the world considers wire nuts so bad they're illegal. In Europe (my employer sent me over here temporarily) there are no wire nuts; everything is done with very secure, basically foolproof screw connectors commonly called chocolate blocks, because they look like one, and you snap off as much as you need.

I don't know if you can even get them in the US, but I'm going to bring a few back with me.

Reply to
TimR

The best information on aluminum branch circuit *connections* I have seen is at

formatting link
branch of the site metspitzer posted) The advice is for a wide variety of fixes, from minimal to replacement (including pigtailing). The information is based on extensive testing for the CPSC (which was apparently headed for a recall of aluminum wiring). .

. One of the failures, which is probably still shown on the inspect-ny site, is aluminum wires with a wire nut on them. There is enough oxide that direct contact between wires is minimal. The spring on the wire nut cuts through the oxide with the current then through the spring. The spring is not intended to be current carrying, and a couple turns of spring turn into a red hot space heater. (This comes from the testing for the CPSC.)

AFCIs (since this year) can detect arcing at loose connections. They won't detect "glowing" connections as above.

The advice for pigtailing in the paper above is apply antioxidant, abrade, twist, apply wire nut. The paper has recommendations for wire nuts and antioxide. .

. Interesting information on Ideal.

Alumicon should be available on the internet. The screw deforms the aluminum which should break through the oxide. The same happens in connections for bigger aluminum wire (though some manufacturers recommend abrasion there also).

Was there a problem with aluminum branch circuit wire? UL thought so. About 1971 they removed listing for aluminum wire and devices. New standards had a different alloy (as dpb wrote) and CO/ALR devices. The majority of the wire installed is the "old technology" stuff. The worst problem was probably "old technology" wire with steel screws on devices.

The risk dpb refers to (as estimated by the CPSC) is that homes wired prior to the revised UL standards (1972) are "55 times more likely to have one or more connections reach Fire Hazard Conditions than is a home wired with copper."

Reply to
bud--

If all the hysteria surrounding aluminum wire was valid I would expect all the aluminum wired homes would have burned down by now.

Reply to
gfretwell

snipped-for-privacy@aol.com wrote: ...

A 40:50X relative risk simply demonstrates how reliable electrical wiring tends to be...

I believe there are something like 40- to 50,000 electrical-related fires annually--I've no real number of the total number of residences for the denominator but it must be in the 10's of millions...

--

Reply to
dpb

So you are trying to say that out of 40,000-50,000 fires a year, only ONE THOUSAND involved copper wired homes That is what 40-50x means for you math challenged

This is still a scare story from a home inspector web site (inspect-NY) and a political organization (CPSC) NFPA and U/L express concerns that the proper wiring devices are used and that the work is done by professionals but they do not have the "sky is falling" attitude I see in these articles. The Ideal 65 wirenut is an example. It is still listed. I agree the Alumicon is a better device but I think CSPC recommending Copalum as the "only" solution may have more to do with a well placed campaign contribution than science.

If you like to dig up statistics, see how many fires have occurred in aluminum homes in the last 20 years where harry homeowner did not alter anything. I bet you will find sloppy installations caused most of the early aluminum fires and if nobody screwed with it, a good installation is still working fine. CO/ALr devices pretty much made the problem go away in houses wired with them. The brass screw expands and contracts at virtually the same rate as aluminum so it doesn't have the creep problem you have with the regular steel screw. A properly made joint is gas tight so there is no oxidation. In fact, in testing an aluminum wire in an aluminum lug like the Alumicon actually performs better than copper wire when thermal cycled ... noalox or not.

If you have an aluminum wired house you should be vigilant to arcing problems and I would even go as far as looking at the devices with an IR thermometers (pretty cheap these days. But I would not get crazy about it and I wouldn't start pulling things apart "just to check". I still believe that once they shook out the sloppy initial installations, most problems were handyman inflicted wounds. BTW AFCIs are pretty much useless for aluminum type failures. There is still the promise of a "series" fault detector but I don't think any have actually hit the street. That is not what "combination" means.

Reply to
gfretwell

You can come back to the US and convert the native population to European technology? Kind of like when they used to send preists to the heathen nations.

Reply to
Stormin Mormon

Nah, but I'll bring back enough to do any of my own u-do-it projects.

In the discussion of aluminum wiring much was made of improper installation. Well, wire nuts are inherently difficult for the amateur to install properly, and not that easy for the professional, though often taken for granted.

There are least two reasons they are not acceptable in Europe.

One is that they are uninspectable. After you put a pigtail together, you really have no idea how much wire stayed in contact under the wire nut, if any. And even if you don't want to admit you never screwed up one of these yourselves, you must have seen a bad job by others. This is especially true with solid or mixed wire, not so bad with stranded maybe.

The other is that the clamping pressure is indirect. While it depends on how hard you twist the nut, the force is caused by the thickness of the wire bundle and how far in to the wire it goes - and you can't tell either under the wire nut.

while you can certainly use the wrong size chocolate block or not do it tightly enough, you can see the screw forcing the wires together, and the harder you turn the screw the harder they press. It is a very secure and checkable connection method.

I bet if wire nuts were transparent they wouldn't be as popular.

Reply to
TimR

I guess the billion or so that work tend to make people believe in them here.

Reply to
gfretwell

. Apparently the politicians at the CPSC invaded UL and cause the removal of listings for aluminum branch wire and aluminum listings for devices.

The CPSC contracted with an independent research laboratory to investigate aluminum connections, with supervision by a professional engineer. Many thousands of connections were tested. Among the findings was that "properly" made connections could fail. The testing was apparently extensive enough for the CPSC to initiate a recall.

In the inevitable lawsuit the court ruled that aluminum wire was not a "consumer product" and thus not under the purview of the CPSC. The CPSC had also started a preliminary investigation of FPE breakers, and this ruling was probably one reason the investigation was closed.

The last time I looked, most of the information on aluminum at the "home inspector web site" was derived from the CPSC investigation. I find your comments discrediting the "home inspector web site" and CPSC far below your usual very good posts.

From a Mike Holt newsletter, referring to the "home inspector web site":

"This website contains extensive information for consumers and building professionals regarding aluminum electrical wiring in residential properties. The contents are the result of study of this topic and represent the opinion of the author. Actual documents, authoritative research, and government resources about aluminum wiring are here. This is the most extensive and authoritative Internet information source for aluminum wiring and related hazards."

And from Mike Holt (on FPE breakers), referring to the "home inspector web site":

"Mike Holt's Comment: The failure rates for these circuit breakers are significant, see the CPSC study. For Additional information about this problem, visit the excellent website

formatting link
managed by Daniel Friedman
formatting link
".

. I didn?t see a "sky is falling" attitude in the paper written by the professional engineer and based on the extensive research:

formatting link

. The OP thinks the use has been restricted by Ideal. (I haven't looked). .

. I believe COPALUM came out best in the extensive testing done for the CPSC. Perhaps you could deal with facts. Alumicon is quite new. [I would use pigtailing, not COPALUM.] .

. You may (or may not) be right. Would be nice if stats were available. .

. One of the advantages of Alumicon is the screw deforms the wire which breaks any oxide layer. The binding screw on a normal device can leave the oxide layer. Not obvious to me that a "properly made joint is gas tight". .

.

I have not looked at other manufacturers, but SquareD has had "combination" AFCIs out since 1-1-2008 (when "combination" types were required by the NEC). I would be surprised if many other manufacturers didn?t have them too.

In late stages of connection failure there is likely to be a series arc. Earlier stages, which can produce plenty of heat, it is a "glowing" connection. An AFCI may (or may not) catch a glowing connection when damage causes ground leakage and the AFCI trips on 30mA ground fault detection.

[Note the problem is 15 & 20A branch circuits only.]
Reply to
bud--

I don't argue about religion and this is what the aluminum scare has become. A cult religion. Rock on

Reply to
gfretwell

Not believe so much as take for granted.

Look here.

formatting link

It's not so much that wire nuts can't work, just that there's a more secure and more foolproof way, at about the same cost.

Reply to
TimR

. What a well reasoned technical argument. It fits in well with your comments about the CPSC and the the "home inspector web site".

Reply to
bud--

I guess I prefer real life statistics to 20 year old reports. Where are all these fires?

Reply to
gfretwell

TimR posted for all of us...

Huh? Link to model airplane club?

Reply to
Tekkie®

Yeah, that was dumb.

I did google image search with terms "chocolate block electrical" and got a nice set of photos of chocolate blocks, then cut and pasted the link which was showing. Hey, i was born before 1980 so officially I am a digital immigrant, not a digital native.

Reply to
TimR

. As I said, it would be nice if stats (one way or the other) were available.

Reply to
bud--

That is why I am skeptical of the CPSC articles. This is the same culture that killed the Corvair ... for no particular reason. It was certainly as easy to roll a 60's era VW bug and they left that one alone. I smelled politics there too.

NFPA should be the people who have the fire statistics to make or break this "problem" and they have never outlawed aluminum wire or the Ideal 65. You could wire a house tomorrow with AA8800 aluminum wire and CO/ALr devices and it would be code legal. I bet you see it happen in the next few years.

Reply to
gfretwell

Wiki says..........

formatting link
(aluminum is misspelled in the link :)

Hazard insurance

In some States, Hazard Home Insurance will not cover homes with aluminum wiring, and some insurance companies that claim to cover it, have a higher premium than homes with copper wiring. Check with your insurance company before purchasing a home with aluminum wiring. }

Of course, that is improperly worded. Many homes have aluminum wire, but not for branch circuits, and it is not spliced to copper.

Even properly made splices with aluminum to copper connections will fail.

Reply to
metspitzer

. It is the spelling used outside the US. Consistent with metal elements ending in "ium". .

. Al to cu branch circuit connections "may" fail. For large aluminum wire the splice devices are reliable with aluminum (if rated for aluminum).

Reply to
bud--