Hi,
My 6 kW grid-tie photovoltaic system is going into wait mode when my five ton AC cycles on. I have 200 amp service to the house, but these summer days the line voltage will drop from 240 to 225. The inverter is an SMA 6000U with a minimum grid tie operating voltage of 213 VAC. I think that when the AC cycles on, it either momentarily depresses line voltage below 213, or it just causes the line voltage to change too quickly for the inverter to maintain the sync (either one of these conditions will cause the inverter to "detach from the grid" and go into a wait mode monitoring the state of the grid).
Questions: - Maybe the line drop from the pole is undersized? (does not seem likely given that Edison must have connected it to the 200 amp panel). - How likely would the gauge of the line drop be the cause of this problem? - Does anybody know what gauge a 75 foot 200 amp line drop ought to be? - Has anybody had success in getting their utility to replace the line drop with a larger gauge drop? - Is there anyway to add something to the AC circuit so that it has a "softer start" so it does not depress the line voltage so much?
This is a real pain as the AC cycles about every 20 minutes and causes the array to go off-line for five or ten minutes each time. I am losing a great deal of electrical production and I can't believe it is good for the inverter, either.
thanks,
doug
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
old dirtbeard wrote:

Your 5 ton AC unit will be fed by a 50 to 60 amp 240 vac circuit. You must understand that the LRA (locked rotor amps) for such a unit can be between 120 and 150 amps and the RLA (run load amps) will be between 17 and 25 amps. Your 6 kw power system only puts out around 25 amps continuous current. I don't what the surge rating for your inverter is but I can guess that it is not enough to start a 5 ton AC unit thus it will drop out and wait for the load to stabilize before kicking back in.
[8~{} Uncle Monster
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Can you give the MAKE and MODEL NO of the AC Unit

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Hi,
Yes, thank you, it is a Lennox HS26-060-2P.
The way this grid-tie system works is that during the daytime when the array is producing more elecricity than the house is consuming, it sends the "excess" current back to the grid and spins the meter backwards. During the day if we need more elecricity than we can generate, it draws the shortfall from the grid. At night the meter spins forward just like there was no PV system.During the day, though, the inverter needs to "lock on" to the fequency and voltage of the grid to invert the 380 VDC to 60 cycle, 240 VAC. The inverter can tolerate a grid voltage range of 213 - 262 VAC and a frequency range of only about 59-61 hz.
The panels do not need to fully drive the AC, but when the AC cycles on, it either is dropping the line voltage below 213 VAC or is dropping the voltage so quickly that the inverter loses it's sync on the line. I am thinking that the line drop from the pole cannot supply the start-up volt-amps required by the AC condenser.
Thanks for any help you can provide.
doug
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Have you talked with the manufacturer of the inverter?
Bob
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Hi Bob,
Great idea, but I have not done so yet.
I wanted to make certain that my grid feed infrastrucure was up to par before I started down other channels. If Edison will not upgrade the line drop, I will contact SMA to see if we could adjust the lower VAC threshold for the inverter.
There is a very clear voltage drop at the inverter when the AC cycles on. As Telstra described, the AC unit draws 107 amps on start-up, and I believe that I just do not have "thick enough copper" between the panel and he pole for the surge that the AC places on the line drop.
It was OK before I installed the PV system, but now I have a more "discriminating consumer" on this side of the line drop. :)
thank you,
doug

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 1 Sep 2007 13:10:49 -0700, "old dirtbeard"

You have grossly undersized your power unit.
You need to at least double the size or get you some window units and turn one on at a time.
Who did the horrible design of your system?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

Sorry I was not clearer -- please see the response to Telstra -- the PV system is a grid-tie, it does not have to power the entire house. We generally run a surplus (I have a negative balance of $180 with Edison), but we will draw whatever additional current we need from the grid. When the AC is on, the PV array and the grid are powering the house.
The utility meter runs backwards during the daytime (except when the AC is on) and runs forward at night when we are not generating. The idea is overall to zero-out so you do not have an electrical bill.
doug
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I read somewhere about a power company that didn't like the idea of the meter running backwards. The management considered it buying back power at the retail rate. A ruling by the courts compelled the power company to buy back power so the utility installed two meters, one for power going in and one for power coming back. The customers were credited for power coming back at a lower rate.
[8~{} Uncle Monster
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

In Southern California (I think it is Federal now), the utilities are required to have meters that turn both ways. SoCal Edison has a graduated billing structure where the first 10kWh/day (baseline) are billed at $.07, the next at $.10, and so on until you get 200% over baseline and the rate is over 40 cents per kWh -- it is a killer if you have a pool, central AC, koi pond (pumps run 24 hours a day), etc.
Here anyway, they have to buy it back at the same rate they sell it, so if you produce baseline amounts, they buy it back at $.07, if you produce more, they have to buy it back at the higher rates.
Bottom line, though, is that my billing cycle is 12 months -- if after 12 months I have used more electricity than I produced, I have to pay them. If after 12 months I have produced more than I used, they zero out the account, say thank you (maybe) and we start all over again. They will not actually pay you after 12 months for any surplus. I don't think it is right, but that is where it stands today.
Because we were running 200% over baseline on a significant portion of our bill, it made the ROI on the PV system about seven years assuming no rate increases. The panels are warranted for 25 years, so it is a pretty attractive proposition if you are on a graduated billing structure and you are a heavy user.
More than anything, though, I installed the system because I felt bad about the amount of energy my house was consuming. I installed compact fluorescent bulbs, timers, motion activated outdoor lights, etc., but with the pool and the ponds and the AC, no matter what I did, I was going to consume 800 kWh to 1.5 mWh per month ($200 - $400 a month).
Now I am a net producer of electricity -- I am actually supplying my neighbors with electricity. The nice thing about PV here in SoCal is that AC is a huge consumer of electricity, and that consumption occurs at peak solar hours, so the PV systems are helping to limit the peak consumption spikes when the utilities need it most (ahem, that is if your AC does not cause your PV system to go off-line for 15 minutes out of the hour).
Also if you are a tool head, it is kind of cool to watch the meters, and monitor what you did each day as far as production (before I go to work in the morning I check the inverter and utility meter, and then when I come home I do it again to see how much electricity we surplused for the day.
Cool bright days produce the most power -- the panels lose efficiency at higher temperatures. On my 6kW system, we produce just a little less than one million watt hours per month
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I want my own "Mr. Fusion" reactor.
[8~{} Uncle Monster
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
You need to reduce your cooling costs.
You can do it with an upgrade to a cooling system that captures the earths cooling system -geothermal.
Or if you don't want to spend that kind of money, you can buy several small very high efficiency wall units with EER of 10.7 to 11.5 and put them in the rooms where you spend most of your time - especially the bedroom. You can cool a very large bedroom with 5 amps @ 110v with a 6,000 btu window or wall unit,and leave the rest of the house alone since you are not using it at night. Same goes for the other rooms you move to during the day.
It should cut your cooling bill easily in half.
On Sun, 02 Sep 2007 21:21:08 GMT, "old dirtbeard"

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Why does he need to do that? I think he made it pretty clear he was producing more power than he used.
Bob
wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

What did the system cost you? How much area do the collectors take?
Bob
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Bob,
Well, it takes about 80 square feet per kW (my 6kW system covers about 500 sq feet) depending on the efficiency of the panels. My panels are 200 kW Kyocera and are a little more efficient than some. You need an east, south or west face. Of course the south face is best. The optimal angle depends on your latitude, but will be greater than 0 and less than 90 degrees.
The price is more difficult to provide because of the rebates, tax incentives, size of the array, amount of electricity you are forecasted to produce, and much of this varies by state and even by county and your utility company. Bottom line is that nobody will pay anywhere near the full retail cost of the system. Since I signed my contract last year, I actually received a better rebate than what California is offering this year. Ultimately they would like to wean the solar industry off from this rebate support, but the technology is pretty stable and I do not see any major price decreasing break throughs occurring in the near future (you do not need to worry that next year someone will come out with a panel that is twice as efficient or costs half the price). This market is not like IT/computing areas when the best time to buy always is in the future.
The retail cost of my system (30 200 watt Kyocer panels, 6kW SMA inverter, permits, installation, all materials, etc., was close to $45K. There was an immediate $15K rebate at the time of purchase, so the initial OOP was $30K. By the time the federal and state tax deductions kick in next year, and the other incentives, it should be about $18K. For me it will take less than seven years to break even.
It pretty much is a cost per watt basis. If you are using less than 1mWh/month (which most people would), then you could put up a much smaller (much less expensive) array. Again, if you are on the graduated billing structure like we are, then to a large degree, the smaller the system, the faster the ROI (because it will be chewing away at the highest cost watt hours). On a graduated billing structure, the closer you drive your bill towards zero, the lower the ROI from the system.
Some areas are on TOU (time of use) rates and your consumption and generation rates are based upon the time of day (peak hours cost and pay more, off-peak hours cost and pay less). We are not on a TOU basis here, but that is something you should check into before you sign any contracts.
I hope this helps.
best,
doug
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Yes. Thanks for the info Now if only I can get the neighbor to remove those 3 poplars.
Do you do any thermal solar for hot water?
Bob
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Now there is an interesting question....
Is it a net benefit to the planet Earth to cut down 3 trees so the solar panel can work?
Mark
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Since the tenant covered the bottom 2 feet of the trunks with dirt when he landscaped, I worry about the trunk rotting, and the trees falling on my house or garage.
And there's always the heat provided by the wood after the trees are cut. But then again, they are poplars.
Bob
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
As can be seen from the Service manual 1ph LRA is 107A and RLA 20A 3ph LRA 88A RLA 12.5A. and unfortunately Modifying the refrigeration circuit to provide unloading wil not significantly reduce those figures. In addition the motor starting can only be XL across the line.There are various approaches to this problem ( Resistance start ) ( Auto transformer ) ( VSD ) but the manufacturer Lennox should be consulted before these are applied.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Telstra,
Thank you -- it is single phase and your information is very helpful in determining the gauge required for the drop loop from the pole.
The AC cycling on does cause the lights to dim when it starts up, and at 107 amp start-up and whatever the furnace blower takes, I can see why I am having issues.
Thanks again, I appreciate you taking the time to research this for me.
best,
doug