97 Volts on Outdoor Outlet

Our neighbor's house was recently hit by lightning. All that we suffered were blown GFCI's throughout our house. After replacing the GFCIs, all outlets are measuring 123 volts as normal except for one. The outdoor outlet is measuring 97 volts and will not power anything. Any clue what's wrong here?

Reply to
O.B.
Loading thread data ...

Hi, Are you using analog meter?

Reply to
Tony Hwang

You probably have a fried wire somewhere in either the hot or the neutral side of the line feeding the outlet. First, disconnect both the hot and neutral wires at the house end, then tie them together at the outdoor outlet and measure the resistance at the house end. Should be less than 1 ohm if the wires are ok.

Reply to
hrhofmann

Even though he thinks he has disconected both wires at the house end, lots of things could go wrong doing that, like disconnecting the wrong wires. He should first measure the voltage between the two wires before tying them together. If the wires really are disconnected, the voltage will be zero, even with an analog meter. At least it will be a lot lower than 97.

Reply to
mm

If the outdoor receptacle is a GFCI type, the power to it is likely coming from the nearest outlet, on the inside of the house. Check to see that the connections are good on that outlet, and any other nearby outlets

Reply to
RBM

He's asking because digital meters have such high resistance that they will read odd voltages picked up as "crosstalk" from other nearby wires. If you are using a digital meter you need to have a load on the circuit like a lamp.

Reply to
jamesgangnc

Let's do this by the numbers:

  1. If the outlet doesn't measure 115-125 then the actual reading is zero irrespective of what the meter says.

  1. When the actual reading is zero, you have a broken connection.

  2. This broken connection is either at the outlet itself or upstream.
Reply to
HeyBub

Ive been hit by lightning, if you suffered Gfis blowing you suffered alot more but it may not be evident yet and you didnt check everything. Things will start failing over the next year or less, its time to check everything electronic and think about that policy you have that covers lightning damage.

Reply to
ransley

I second the suggestion to check with both an analog and digital meter.

Digitals meters often pick up parallel line voltage ghosts.

Reply to
mike

It's not whether it's a digital or analog meter: It's what the input impedance of the meter is. My old Triplette with a mirrored scale will read nearly the same voltage as my Fluke on similar scales because they have similar input impedances on those ranges. A light bulb, any resistance across the wires will kill the voltage if it's just a phantom voltage. In fact, so will a 47k, 100k resistor and even higher, depending on the situation. I use 47k; high enough to kill the voltage but not low enough to quickly burn, even snap, if it's a real voltage for some odd reason. Phantom voltages cannot light a light bulb's filament either; so if it glows, there is a real voltage there.

Twayne`

Reply to
Twayne

My guess is you are using a digital meter. They have a very high interal resistance that means they can measure false high voltage. Do you have access to an old analog meter. They blead off induced current. You can do the same thing by putting a small load on that circuit, like a 120V test lamp. Chances are it will not light that test lamp or move the analog meter.

Assuming the above is correct, then you have a connection problem (open circuit) somewhere between where you are measuring and the power source.

Reply to
sligoNoSPAMjoe

Good, correct information. However in general the dividing line is between digital and analog.

Afer reading your reply, I realize that it is possible, if someone assumed my comments were 100% right, could get themselves in a dangerous situation. I stongly suggest that no one assume the independance base on the type of display.

Please anyone who is not sure about all this, be very careful. If you are not sure, you liekly should not be using the meter.

BTW I once worked for a man who thought he knew what he was talking about and burned down his own business, because he did not understand what happens with a floating neutral. Lucky no one was injured.