I know that you cannot use 14 gauge wire in a 20amp circuit because 14 gauge can only handle 15 amps, but I ran into a problem with my bathroom remodel. I have a huge mirror on one wall that also has a vanity bar light on it that was stuck on the mirror with adhesive. The idiot who put the mirror on did not cut out the box opening, but rather just cut out a 1" hole. The wire feeding behind the mirror is a 14 gauge wire. There is no way I can get a 12 gauge wire inside the box because of the small opening in the mirror. And I can't even use the 14 gauge as a drag line to pull because its clamped in the box, and plus it's fed from the bottom. So my question is being that since the vanity light is the only load that the 14 gauge wire is feeding, any problem with tapping off the new 20A circuit that I ran? I figure the thin wiring inside the vanity would fry first anyway before the 14 gauge would if there was a problem. Otherwise I would have to tear down the mirrored wall to get to the box.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Mike,
Why did you run a new 20 amp circuit to power one light bar? I'm not sure if that's what you are saying but I can't figure ir out. Replace the 20 amp breaker with a 15 amp breaker and you will be ok. If you need 20 amps on that circuit for some reason then you can not use the 14 gauge wire. If a short circuit happens in the light bar the wire may overheat before the breaker blows. Can you go through this wall from the other side to acess this electrical box, then patch the hole and repaint? Might be easier than attacking the mirror.
Dave M.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Before the remodel, the bathroom was fed by a 15A circuit, which was also shared by the outlets and lights in the adjac ent den. So I ran a new 20A circuit to feed the GFI outlet, bath fan and shower light. But the vanity light is the only box I can't access. It's on an outside wall so I can't get it on the other side.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Holy cow, I've run into that same mirror guy... several times. I doubt you'd fry the #14, but why not just connect it to the existing 15 amp circuit that is feeding the bathroom now. Only the outlets are required to be 20 amp
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Good advice, the real answer.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@aol.com wrote:

And if the GFCI trips he will still have lights powered on which is a plus.
Kevin
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

..
The way this thread reads is that the previous wiring for the light is still there. The one inch hole is not code compliant; but anyway, why not just leave the light hooked up as before! Separate circuit.
If that is not possible, hook up the 14AWG wiring to the mirror light fixture to the 20 amp circuit wired with 12 AWG and change the circuit breaker for the bathroom circuit to 15 amps.
Surely 15 amp at 115 volts, a total of 1700 to 1800 watts is sufficient for whole bathroom?
Even a hair dryer (plugged into the GFCI of course) will take say a maximum of 1300 watts leaving at least 400 watts for everything else!
Everything in our bathroom uses no more than 500 watts at most, even if all the lights are on including one over the shower and one is electric shaving at the same time.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
what if a person has a 1500, 1800, or 2000 watt hair dryer? Then i guess your calcs would not work eh?
s (Amazon.com product link shortened)
The way this thread reads is that the previous wiring for the light is still there. The one inch hole is not code compliant; but anyway, why not just leave the light hooked up as before! Separate circuit.
If that is not possible, hook up the 14AWG wiring to the mirror light fixture to the 20 amp circuit wired with 12 AWG and change the circuit breaker for the bathroom circuit to 15 amps.
Surely 15 amp at 115 volts, a total of 1700 to 1800 watts is sufficient for whole bathroom?
Even a hair dryer (plugged into the GFCI of course) will take say a maximum of 1300 watts leaving at least 400 watts for everything else!
Everything in our bathroom uses no more than 500 watts at most, even if all the lights are on including one over the shower and one is electric shaving at the same time.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Complicating things more is that the vanity light, and the rest of old bath circuit was buried in a junction box in the ceiling I found after taking down the sheetrock. So I only have a 3 foot tail out of the vanity, which means I need a junction box if I was to reuse it again. I'm going to give it another shot tonight. Maybe if I'm persistent, I can get the new wire in the box.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sep 17, 11:55am, "Steve Barker DLT"

Ok. Valid point about maximum wattage calculations.
But didn't know that North American 115 volt hair dryers come in such high power versions! The only ones have seen here (Canada) have been around 1300 watts IIRC. Maybe am out of date here? Although some Canadian electrical codes occasionally seems to be a bit tougher than USA and UL etc.
Only the hair dryers and other appliances I have seen in 230 volt countries seemed to be more powerful and would possibly not North American UL etc. code compliant anyway? You should see how fast a 2 kilowatt kettle, with a few litres of water in it, boils!!!!! Especially when the 230 volts is a bit on the high side! Perhaps 10% or so high; thus instead of wattage proportional to 'Voltage squared'; 230 x 230 = 52,900/R one gets 253 x 253 = 64,009. 64/52.9 = some 21% higher!!!!
And yes; 2000 watts is 17.39 amps (2000/115 = 17.39 amps). Since it is a heater with a little fan motor that's mainly resistive. That is a little more than the recommended 80% of the rated 20 amp capacity of a 12 AWG circuit though. i.e. 0.8 x 20 = 16 amps.
So 17.39/16.0 = 1.08. That's about 8% over recommended normal load capacity. Although it shouldn't cause any problems provided everything is in good condition and not much else, maybe a couple of light bulbs, is plugged in/switched on on same circuit.
Thanks for the comment. Still feel that 115v x 15a = 1725 watts should be plenty for most entire bathrooms!
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
just a short comment about your 80% comment. That would only apply if you use a hair dryer for over 3 hours at a time. The 80% rule is for 'continuous' duty, which is defined as anything over 3 hours at at time.
s
And yes; 2000 watts is 17.39 amps (2000/115 = 17.39 amps). Since it is a heater with a little fan motor that's mainly resistive. That is a little more than the recommended 80% of the rated 20 amp capacity of a 12 AWG circuit though. i.e. 0.8 x 20 = 16 amps.
So 17.39/16.0 = 1.08. That's about 8% over recommended normal load capacity. Although it shouldn't cause any problems provided everything is in good condition and not much else, maybe a couple of light bulbs, is plugged in/switched on on same circuit.
Thanks for the comment. Still feel that 115v x 15a = 1725 watts should be plenty for most entire bathrooms!
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Close, but no cigar. The Code applies the 80% rule to "continuous load" which it explicitly defines as a load expected to operate _at_maximum_current_ for 3+ hours.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Well _THANK YOU_ for splitting that hair.
s
wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

No pun intended? (hair dryer)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

The point is, that it takes more than just a three-hour duration to invoke the 80% rule.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Thu, 18 Sep 2008 11:48:29 GMT, snipped-for-privacy@milmac.com (Doug Miller) wrote:

If you really want to get technical, 210.23(A)(1) says
Cord-and-Plug-Connected Equipment. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.
"Continuous load" is not mentioned
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
http://www.google.com/products?q=hair+dryer+wattage+&btnG=Search+Products&hl=en&show
Yes, plenty of them.
--
Christopher A. Young
Learn more about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Wed, 17 Sep 2008 09:02:46 -0700 (PDT), terry

They don't. This is the same creative rating method they use to make 6HP compressors that plug into a 14a receptacle.
http://esteroriverheights.com/electrical/1875w_hair_dryer.jpg
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@aol.com wrote:

Is the meter a true RMS type or averaging (cheap) type? The marketing people will use whichever gives the higher reading. Kevin
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

For the 3 hour explanation. I learnt something. Thanks. Fortunately leaving a low wattage curling iron plugged in plus the short term use of the hair dryer should be fine. Also to my mind there is always difference between something one does temporarily which is 'right at the limit' and something that is not in accordance with code for the long term for use by those who do not understand. For example using a welder intermittently on a too small or too long an extension cord and getting away with it because you have someone else watching. The extension wire is outside in free air and if it did catch fire you immediately disconnect and since you are welding have a fire extinguisher at hand!. Compare that to someone who incompetently hooks up their clothes dryer with wrong AWG and puts pennies in place of blown fuses! Yup seen that! Also seen every appliance in a rural kitchen plugged into the ceiling light socket using a Christmas tree light extension cord! And wondered how with the extension cord getting hot the fridge ever got enough voltage to start! "Yes ma'am that's why the TV goes to about half width each time the well water pump starts". But it's amazing what WILL work at times; just! Was at a home construction area yesterday; three 115 volt extensions across the street, we just drove over them, plugged into one extension box from a completed home! At a glance all thee looked to be the usual 18 or 16 AWG all plugged into another that at best was #12; maybe #14? "Hey boss this skilsaw don't cut too good"! :-)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Site Timeline

Related Threads

    HomeOwnersHub.com is a website for homeowners and building and maintenance pros. It is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.