Sat. 7/7/7 service call western ma.
M: mb2436L S:# 0005a4936
These systems run at a lot lower cfm/ton then a normal AHU, dont they. Here's my situation. Another tech was at the customers house yesterday and found evap. iced up heavily and removed a totally glogged filter. I had to return today to verify operation after a night of letting the evap thaw. He told me to look for a leak which he insisted they was. These were my readings.... R-22 TXV OAT 69'F Head psi 175 (92'F condensing) lig. line tmp 87'F SAT 42'F RAT 66'F Suct. psi 59 (33'F ) suct. line tmp 63'F ..suct. line tmp out of evap 54'F.
Think this is low on charge??? I don't think it is but just looking for other inputs. My condenser-split (ambient to condensing tmp) isn't bad 23'F on
10 seer condenser, pretty clean too I can see right through the fins. 24'F TD across my indoor coil (these unico's run a lot lower cfm/ton airflow dont they?) 30'F of superheat which hmm... not really much load on that coil with 66'F return temp... not sure what to think of that. About 5'F of subcool which I guess isn't all that bad, no name plate info regarding subcool on the condenser to what it's looking for. I'd think I would have a little more with not much load on the evap. Piping from the condenser goes straight through the wall into the basement, not like a 40' vertical lift or anything. J