Please Help......New tradesman trying to diagnose this problem.....This system was installed may of 06 and since we have had

3 txv valves go bad. Before I change this valve again, this just sounds to weird..... Am I missing something? Any help would be greatly appreciated.....Thanks in advance!!!!
Reply to
brent
Loading thread data ...

Brent; PJ is right if you want some one perhaps try to help you you need to give little more info. what type system is this does unit have solenoid in liquid line does unit run constantly does unit cycle on and off does unit have hot gas bypass does unit have auto. pump down what temperature is this system design for what is the application what refrigerant is use on what type control does it work of: ON/OFF or PID what is temp. deviation if works on ON/OFF controll what is pressure running what is pressure stand by what is pressure beginning of cycle what is the pressure at the end of cycle what position is TXV mounted vertical or horizontal what type of TXV is this internal or external equalized what is temp. at thermal bulb beginning of cooling cycle what is temp. at thermal bulb at the end of cooling cycle

you answer all these questions and perhaps some one will be able to gave some idea to the cause of your problem

Good luck from Dido

Reply to
AKS

"AKS" wrote

And don't forget to tell him about CLOSING the return air vents upstairs so the hot air on the second floor will flow down the stairs with the cooler air! Dildo...our A/C newsgroup expert! ROTFLMAO!!!!

Reply to
Bob_Loblaw

Trane XR13 4 ton split

no

no

no

residential air conditioning

residential

R-22

thermostat

standard differential

outdoor pressure is 14.7 psi at sea level

same as above

same as above

same as above

what about diagonally?

non-bleed

there, I answered most of your questions, whats wrong with the unit?

OP: post the model number of the outdoor unit, then the following:

Evap Air inlet temp Evap Air outlet temp Suction pressure at compressor Suction line temp near evap inlet Suction line temp near compressor

Condenser Air inlet temp Condenser Air outlet temp Liquid line pressure (preferably liquid line and not head pressure) Liquid Line temp near condenser Liquid line temp near txv

Once we have these temps & pressures, the system can usually be accurately diagnosed over the internet

You might also indicate for us what position the sensing bulb is located in. If horizontal, at what position clockwise?

Is there a liquid line filter drier in the refrigerant lineset?

If you are serious about wanting help, you first must learn to ask the right questions.....

Reply to
gofish

snipped-for-privacy@gonefishin.net wrote

Hey, these can't be relevant questions! Otherwise, Dildo would have asked them! He's our resident expert, ya know....... :-) Oops! I have to go.... I have to put more fans at the bottom of my staircase to force the hot air back upstairs, ever since I closed the return air vents like Dildo suggested.......

Reply to
Bob_Loblaw

I did not say that I will solve problem But YOU have posted more questions You are Pro. So how about give us solution Thank you Dido

Reply to
AKS

No I am not but you are So smart ass give us solution to the problem DIDO

Reply to
AKS

"AKS" wrote

That's one of many differences between us... I don't try to answer a question if I don't know the answer.....you do.... and that's what makes you a Dildo!

Reply to
Bob_Loblaw

Dildo say that!

Reply to
Oscar_Lives

For one thing, exactly what is happening when the valves "fail"?If they are acting like they are closed off and the unit is pumping down into a vacuum, and then the system works ok for a while after the valve is replaced, the system most likely has crap in it plugging the valves up, or it has moisture in it and is freezing up at the valve when the load drops and the suction pressure gets down much below 60. BTW, I am assuming you are talking about the valve on the indoor coil, or is this a heat pump and it is the outdoor valve? We have had several of them (that new style HP OD valve) that were DOA on brand new units, though I am not aware of any multiple failures. Larry

Reply to
lp13-30

When we get the needed information to the CORRECT questions... someone will.

Reply to
<kjpro

Solve a problem BEFORE getting required info?

Oh where is that crystal ball????

Reply to
<kjpro

Come On, Dido! use your weapon now! show them your belly button tattoo!

formatting link
Bob

Reply to
DIMwit

Trane has had many problems with their expansion valves.

Try using a Sporlan TXV or drop it for an orifice.

Reply to
B-Hate-Me

We already probed orifices with Dildo or? Dildos orifices?

Reply to
Tekkie®

Shit man, common sense...

In the absence of any other diagnostic tools, can always simply "feel the pipes"--your looking to find some place where the heat unexplicitly stops moving...

Reply to
Jeffrey Lebowski

How do you know it&#39;s a bad TXV? What are the symptoms?

Some temperatures and pressures are helpful to us guys on the other end of the computer.

You do have a liquid line filter drier right before the TXV, right?

Reply to
Stormin Mormon

I hope you have found what you was looking for I do have problem with hemorrhoids

Reply to
DIDO

You are a hemorrhoid and a fissure all in one!

Reply to
Oscar_Lives

My friend you seem to be with experience in that line perhaps you can give us some pointers how is being one

Reply to
DIDO

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.