Reply: Condo Trouble Shooting Cooling - All Original Posts Disappeared here
What is the temperature Spit of the outdoor condenser air discharge? A 12-SEER outdoor condenser air temp split should normally be around
18/20 to 24-F heat rise split.All I saw were temperature reading, NO pressure readings. We need Indoor Return Air Wet bulb or %/Humidity Readings No refrigerant line temps, NO Superheat & Subcooling figures! Review the trouble shooting Superheat & Subcooling and give hard copies to the techs & engineers.
We are NOT there therefore, we have to know all the airflow CFM, all the Pressures. & temp figures to even guess at what is wrong.
How many supply diffusers are there? If the ducts are too small and the diffuser's engineered for high velocity and a long throw, it might feel like you are getting a lot more airflow than is actually being delivered to the rooms. There could be an airflow /ductwork problem.
It also could be too much airflow unit charge when condo was hot resulting in a horribly overcharged system! Read my linked page:
Also, static pressures should be taken and compared to the blowers curve graph or chart!
- udarrell - Darrell