Cooker circuit query.

My cooker circuit is currently fused at 30A and supplied by a (rather ancient) 4mm cable. As part of the rewiring the circuit will now be fed from a 32A MCB and my electrician has suggested using two new 2.5mm cables to supply it instead.

While it seems to make sense to me, I'm a little worried that he's only suggesting it so that he can use up the 2.5mm he's got left...

I'm probably being a bit too paranoid and I'd be very grateful if someone could please confirm whether it is acceptable to use two 2.5mm cables in this fashion.

Many thanks,

Ben

Reply to
Benjamin
Loading thread data ...

2.5mm is good for 27amps IIRC. What's the wattage on your cooker?

Both my hob and oven are on separate 4mm cables.

Mike

Reply to
Mike

Are you sure that he is a qualified electrician and Part P registered. ?

Sounds like a ruddy cowboy to me

Reply to
the_constructor

That would be my take on it too. I don't know much about the latest wiring regs but I would have thought that paralleling cables is not considered best practice. What happens if one cable works loose or is accidentally cut frinstance?

Reply to
malc

My instinct is that you should insist on a single cable, 4mm.

IIRC, the load the cable can safely take is proportional to the cross-sectional area. So 2 x 2.5mm sqrd gives you 12.5 mm^2 but 4mm sqrd gives you 16mm^2. The actual copper core diameter is much less than 2.5 or

4.0, but I guess the principle holds good.

Also, shouldn't the fuse (or trip) be rated to protect the cable? - so the cable has got to be safe at 32 Amps.

Reply to
Martin

Cooker circuits are normally wired in 6mm t&e not 4mm and fused at 32a. Ring main circuits are normally wired in 2.5mm t&e fused at 32a. At the breaker of a ring both cables (2.5mm) are connected together as they are at each socket outlet hence the term ring.(very few work loose)

Whilst very uncommon running a 32a cooker circuit as a dedecated ring is not (as far as I am aware) against any regs'

However unless your cooker is miles from the mains the cost of a length of

6mm is nothing compaired to the hastle of running 2x2.5mm cables as a ring. And most sparks carry 6mm as stock.

HTH CJ

Reply to
cj

It isn't quite like that. The quoted size of conductors refers to sq mm in area, therefore 2.5sqmm x 2 = 5 sqmm, whereas 4 is just 4. Having said that, I would use 6.0 to give bags of safety factor. You may have a bigger cooker in the future.

Steve

Reply to
shazzbat

Ah - that makes sense. Thanks for putting me right....

Reply to
Martin

Using 6mm or indeed 10mm on some cookers is the norm.

You forgot about the earth loop. Two 2.5 T&Es have a combined cpc of 3mm, whereas 4mm I think (never bought any) has only 1.5mm cpc. It would be possible to use longer runs using two 2.5mm cables.

Regardless, insist upon 6mm as the minimum size.

Adam

Reply to