UFER electrode question


I'm using the rebar in my storage shed/well house as the grounding electrode. I just read that the footing has to be in contact with the earth, which means that I'll have to pull back the plastic that I have extending across the footing. Question: Is it sufficient to pull back say 25 feet of plastic(the UFER has to be 20' long (it will be the entire perimiter rebar), or should the entire footing be on the dirt?
Thanks, Bob
--
Robert Olin
Bob's Water & Septic LLC
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

*Soil conditions vary by region which affects the ground resistance therefore the more contact the better. However I just read 250.52(A)(3) and the way I interpret it you are fine with 20'. Your best bet is to contact your electrical inspector and ask him.
In addition to the above you could also take two ground rods and lay them in the trench along side of the footings as long as they are at least 30" deep and at least six foot apart. 250.53(B) and 250.53(G)