mobile home furnace runs constantly.

No manufacturer or model number. Fan and heater coils run constantly until breaker is turned off and left off for a while. Then runs fine for awhile and does it again. Even with thermostat set to cool coils heat and fan runs. Replaced temp sensor and single double stack sequencer last fall. Thank you for any ideas. Curtis W.

Reply to
Curtis W.
Loading thread data ...

Locatet the thermostat wires that come from the thermostat to the furnace. Provided this is not a heat pump and the unit is wired correctly, disconnect the white thermostat wire while the unit is heating. Wait about 4 minutes. The unit should be off by that time. If it is you have a problem with the thermostat or the wires between the thermostat and the furnace. If it continues to run after the 4 minutes with the white wire disconnected, you have a problem with a control in the furnace or a improperly wired heat circuit.

Reply to
stanhvac1

Thank you Stan will try, Curt

Reply to
curtis_w

Sorry I haven't responded but I haven't been on here lately. I don't know if you have checked anything yet, but let me know if you need any more information to narrow down your trouble issue.

Reply to
stanhvac1

Thank you very much Stan. Problem has not repeated but I have saved your advice. Curt.

Reply to
curtis_w